Viessmann Vitola 200 w/ Riello Stack Temp @ 254
shoudabeenaplumba
Member Posts: 74
in Oil Heating
I was in a mechanical room the other day drooling over a boiler combo I've comtemplated for my home (If money wasn't a concern). Viessmann Vitola 200 w/ a Riello F10 burner. It was a mixed system with both radiant floor and baseboard. The service folder was there so I started checking it out and noticed on the factory burner test sheet the gas anaylsis was as follows:
T. Air- 74F
T. Gas-254F
O2- 4.1%
C02-12.5%
I couldn't find any notations from the installer if he'd corrected this, but why would the factory test be set up like this? In the brochure for the boiler it states a net stack temp of 329 degrees with a water temp of 167. I know this boiler is supposed to be great at handling ultra-low return temps, but what about stack temps. Could too low a stack temp harm a boiler with no low limit?
Is the danger in low stack temp really about protecting the flue liner?
T. Air- 74F
T. Gas-254F
O2- 4.1%
C02-12.5%
I couldn't find any notations from the installer if he'd corrected this, but why would the factory test be set up like this? In the brochure for the boiler it states a net stack temp of 329 degrees with a water temp of 167. I know this boiler is supposed to be great at handling ultra-low return temps, but what about stack temps. Could too low a stack temp harm a boiler with no low limit?
Is the danger in low stack temp really about protecting the flue liner?
0
Comments
-
Vitola
Vitola won't condense in the boiler but the flue is still a problem. Use a liner or the chamber insert has spots to drill out to increase stack temp if necessary. If you are going for a Vitola.go Vitoflame!To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
So the weak spot .
Is the flue? Depending on the cost to reline I would think it would be cheaper in the long run, just not for me I only burn about 1000 gallons/yr so I'd be looking at 10+yrs payback to line my chimney instead of losing 3% on the efficiency. I just can't stand the thought of having to LOSE efficiency.0 -
10 years too long?
Tell me where you can get 10% tax free,risk free? A lot better than my .45% money market account!To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
Gotta line the chimney
In some states, the chimeny must be lined on every boiler installation. I have done a large number of Vitolas and they are the cat's meow. I try to set my stack temps at around 325. The boiler can handle return temps down in the 70 deg F range but the chimney can't.
As mentioned before, there is a place to drill out holes in the back of the stainless steel chamber.
Good luck.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements