Indirect tank in the summer question
russiand
Member Posts: 75
I am seeing a condition with my indirect that I don't quite know how to address. In the warm months when there is no call for heat from any zones other than the indirect, boiler water can get significantly colder than water in the tank. When the aquastat in the indirect calls for heat, there is a period of time when cold boiler water circulates through the indirect's heat exchanger, effectively robbing the indirect of its heat. In a mater of mintures boiler water obviously warms up and everything works as normal. Is there a way to delay circulation of water through a zone untill boiler water reaches a certain temp? In the winter this is not an issue since boiler water on average stays pretty hot. I am uzing a Taco ZVC with priority for the tank.
Thanks in advance.
Thanks in advance.
0
Comments
-
Very good question
And one I used to battle with in the summer months with my Plus 30 indirect ( lotsa women in my home ) .
What type of aquastat do you have on the boiler ? What type of boiler ? Worst case - you could add a single aquastat to the boiler to delay the indirect zone valve from opeining till the boiler water is hot . But you get the risk of running out of hot water that way also ........0 -
Indirect tank in the summer
Before you spend any money solving this problem, make sure it is a problem. N.B.: I am not a professional heating contractor.
I have an Ultra Plus 40 indirect-fired hot water tank. This holds a little less than 40 gallons of domestic hot water, and the water jacket holds 6 gallons. The boiler holds about 3 quarts of water and the piping between the two hold perhaps a gallon or so. Call the whole thing 8 gallons. Unless I use a lot of hot water (I rarely do), this means the boiler fires once or twice a day for less than 10 minutes each time.
The way my boiler is set up, the domestic hot water heater is primary, but it does not matter in the summer. The boiler is set to run 160F water into the water heater that is trying to maintain 125F hot water. When the heater asks for water, the circulator turns on immediately and the fire comes on pretty quickly. Since the boiler consumes 80,000 BTU/hour input, it can heat the gallon or two of cold water pretty quickly. Meanwhile, of course, the cold water is going into the hot water heater, but the heat from the hot water heater is not really wasted, since it means the boiler water comes up to temperature all that much quicker. (The pipes between the boiler and the hot water heater are insulated.) So I would imagine the only heat wasted would be that lost from the boiler itself, and it is pretty small (holding less than a gallon of water). Also, due to the design of my boiler, the manufacturer insists on running the circulator anytime the boiler is firing.
Last summer I burned 3.15 therms per month for my boiler and (nominal) 40 gallon hot water heater, but I do not use a lot of hot water (no women in the house).0 -
If your boiler is piped primary-secondary
you can put an aquastat on the primary loop that will cut off the indirect circ until the primary is up to 110 degrees or so.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
System 2000
You can install a System 2000 boiler. It will not circulate water until it reaches 140 degrees. Also it will probably cut your heating bills by at least 30%. Now you can add on a solar package for domestic hot water and save even more and get rebates to boot!
http://www.energykinetics.com/index.shtml0 -
I have a regular L7224U on the boiler
With low diff disabled. The boiler is not piped primary secondary.0 -
INDIRECT
IF YOU HAVE A MODERN BOILER THIS IS NOT AN ISSUE BECAUSE THE BOILER HEATS UP RAPIDLY.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements