Hi All - My boiler system has three zone valves, powered by 24 volts
AC. I am looking to rig up a indicator light inside my home to show me
which zone is currently calling for heat. My thermostats do not have
any lights on them.
I thought of two ways of doing this and am looking for advice on these or perhaps another suggestion.
1) Attach a relay that is powered by 24 VAC to each of the zone valves
on the zone valve power leg, not the end switch leg. Then build a
simple DC circuit on the switched side of the relay to light an LED in
my house.
2) Light an LED for each zone directly from 24 VAC using a circuit like the one in the link below.
<a href="http://www.electro-tech-online.com/attachments/general-electronics-chat/30221d1244816557-convert-24-vac-power-2-5-vdc-leds-3wayled.jpg">http://www.electro-tech-online.com/attachments/general-electronics-chat/30221d1244816557-convert-24-vac-power-2-5-vdc-leds-3wayled.jpg</a>
The second option would be cheaper to implement, but I'm concerned that
extra resistance added into the 24 VAC circuit might somehow interfere
with the proper operation of the zone valve.
Any thoughts or ideas are welcome. Thanks!
AC. I am looking to rig up a indicator light inside my home to show me
which zone is currently calling for heat. My thermostats do not have
any lights on them.
I thought of two ways of doing this and am looking for advice on these or perhaps another suggestion.
1) Attach a relay that is powered by 24 VAC to each of the zone valves
on the zone valve power leg, not the end switch leg. Then build a
simple DC circuit on the switched side of the relay to light an LED in
my house.
2) Light an LED for each zone directly from 24 VAC using a circuit like the one in the link below.
<a href="http://www.electro-tech-online.com/attachments/general-electronics-chat/30221d1244816557-convert-24-vac-power-2-5-vdc-leds-3wayled.jpg">http://www.electro-tech-online.com/attachments/general-electronics-chat/30221d1244816557-convert-24-vac-power-2-5-vdc-leds-3wayled.jpg</a>
The second option would be cheaper to implement, but I'm concerned that
extra resistance added into the 24 VAC circuit might somehow interfere
with the proper operation of the zone valve.
Any thoughts or ideas are welcome. Thanks!
0
Comments
-
Led indicators
Lighting the indicator led directly from the 24VAC feed to the zone valve actuator should be no problem. Using the combination of the 1K resistor, rectifier diode and Led as in the center circuit diagram should work fine. Just remember to connect the indicator circuit in parallel with the valve actuator, not in series with it.0 -
Thanks
Thanks Mike,
To make life easier, I ordered three of these. They already have the diode and resistor built in. Should work well!
http://www.cml-it.com/pdf/4-20.pdf0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements