Vito 100 DHW control

Has anyone tried useing a Taco pump relay (with priority) to look after indirect, or is the Viessman control the only option.
Thanks, Dobber
Thanks, Dobber
If you don't have time to do it right, what makes you think you have time to do it over?
0
This discussion has been closed.
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 562 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 50 Job Opportunities
- 7 Recall Announcements
Comments
Are we talking Vitodens 100? If so, simple...Using a Taco Zone Control EXP version add theTaco PC600 post purge card. Gives you a seperate XX to take back to DHW on the Vitodens 100 to get the boiler into high fire. You wire the zone control no different than if using a conventional boiler. Make sure you leave the priority switch in the on position. The zone control will pick up the card once it is plugged in and run priority within itself. The Vitodens will shut down RT and go into high fire once DWH receives the signal.