Hot water radiant floor User

Illinois_Paul
Member Posts: 1
I am preparing to install some taco 219 Swetchek valves in a system I built and designed 10 years ago. (I didn't think I needed check valves at the time) I have 3 and have had them sitting for all this time. For the most part, the system works OK without them, but it isn't totally up to my standard.
My questions: Why would I need a thumb-knobbed adjustable check valve? I see this type is commonly installed in hydronic heating systems.
Why not just a simple non-adjustable check valve without a manual/open option?
What does "open" mean as opposed to "normal"? Is "open" allow flow either way thus negating check valve effect? Explain why a check valve would have an "open" option? Explain "normal". Taco box instruction indicated, "normal" = "automatic". So, why shouldn't this always be the proper position?
Thanks.
My questions: Why would I need a thumb-knobbed adjustable check valve? I see this type is commonly installed in hydronic heating systems.
Why not just a simple non-adjustable check valve without a manual/open option?
What does "open" mean as opposed to "normal"? Is "open" allow flow either way thus negating check valve effect? Explain why a check valve would have an "open" option? Explain "normal". Taco box instruction indicated, "normal" = "automatic". So, why shouldn't this always be the proper position?
Thanks.
0
Comments
-
taco 219 Swetchek valves
If I understand the Taco description, the #219 Flow Check valve is not adjustable. The knob on the top can be used to open the valve completely to allow gravity flow in case a circulator fails, allowing some heat to be delivered. Since I am not a professional, I do not know how useful that feature is The normal position is to enable the flow-check operation. The Open position allows flow in either direction. The Flow Check , in normal use, prevents flow not only in the reverse direction, but also gravity flow (within limits) in the forward direction.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 67 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements