superheat
ddenny
Member Posts: 75
hello
several times on ac systems with cap tubes or piston metering devices I need to add freon to raise the evap pressure to 60#. but in so doing I get too low a superheat reading. normally I expect the suction line to be slightly cool to the touch. but when the suction line gets very cold I think its because of the freon I added in order to raise the suction pressure to a point high enough to keep the evaporator from freezing. the system will work this way but I don't like that cold suction line. any suggestions of insights?
thankyou
dennis
several times on ac systems with cap tubes or piston metering devices I need to add freon to raise the evap pressure to 60#. but in so doing I get too low a superheat reading. normally I expect the suction line to be slightly cool to the touch. but when the suction line gets very cold I think its because of the freon I added in order to raise the suction pressure to a point high enough to keep the evaporator from freezing. the system will work this way but I don't like that cold suction line. any suggestions of insights?
thankyou
dennis
0
Comments
-
...
Why do you try to get 60# suction on every system? It should be different for every system depending on a number of factors.0 -
superheat
Having a lower than 60psi is a" it depends " situation. A rule of thumb here might help,so,what is the outdoor air temp? Not lower than 70-72*.What is the indoor air air temp? again ,not lower than 70-72-74* Is this your 1st time on this unit?Oversized? Dirty evap,filters,blower wheel?Duct sizing wrong?Supply registers not open?And checking the charge is better done by the subcooling,not the superheat.0 -
dennis
Got your e-mail. I TOTALLY agree with you about Profressor Silberstein' book "Pressure Enthalpy without tears" very good but can't say I grasped all of it .LOL LOL. Again,a rule of thumb, on cool days you can get fairly close pressure readings. On a 50-60* I place a plastic tarp around the cond coil to raise the head press press up to 95* condensing. [r-22 is about 182psi] and then charge the low side upto 60psi or so ,depending on the other rule's of thumb.It's close ,but better than waiting for all of the units for a warmer day. It's kind of like a motormaster head press control.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements