Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Radiant Floor Project & a Radiator?
Kungur
Member Posts: 49
I have started a radiant heat retro fit of my home. I am using the transfer plates system. But I have 1 area, our home office where I do not have access to the underside of the finished floor. This is an area under a run of countertop/desk area where my wife sits. I was wondering about a short length of "radiator" under the desk area. I can snake some pex up to it through a cabinet.
If this is workable what brand of radiator?
Thanks.
Tom
If this is workable what brand of radiator?
Thanks.
Tom
0
Comments
-
Radiator
Other than decorating the wall, it won't produce any heat with water temperatures below 120°.
That's the dilemma of going with plates; there's not much else you can do with water at that low of a temperature.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
hmm.
sounds like the room itself is heated but not the under desk area?
short radiator would be great for that.
ven if the whole room is unheated, a radiator can be sized for it. you can size radiators for anything, if you have enough space. that's the big issue usually.Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.0 -
Kick space heaters
Tom,
You can use a stick of baseboard if you have enough room like Rob suggested you would just run the BTU output calculations with 120 degree water temp for what ever manufacture baseboard you use and size it for you coldest day that way you don't short change yourself.
My home is 2x4 construction and 30+ years old and I run a step rest curve and the old baseboard keeps up just fine when it is -30 the system runs at 165F and when it is 40 the system runs at 109F all you have to have is a delta T to get heat out of baseboard. My home stays a comfortable 70 degrees all the time.
We just finished a remodel on a home where it was radiant plates upstairs and we used Beacon Morris kick space heaters for the basement zones. We ordered the heaters with the low temp aquastats that turns the fan on @110 F and off @ around 95. This way the whole house could operate at the low water temperature of the radiant zones. The kick space heaters are a great way to get alot of heat out of a small unit.
Best of luck to you0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements