tekmar control 360 boil target blank

m206718
Member Posts: 1
i have been having heat problems. the burn stops firing and the error light is not on. when i cycle through the control items the boiler temp is well below the setting and the boiler target is three dashes instead of the number. when i enter the setting menu the target is set. the only way to fix it is to cycle the power to the unit but the fix only seems to last a day or two. if anyone has an answer that would be super
0
Comments
-
power?
How are you powering the control? I once solved an erratic control by giving it its own source of power. MB0 -
power?
How are you powering the control? I once solved an erratic control by giving it its own source of power. MB0 -
Mix Target - - -
The mix target shows three dashes when there is no mix demand signal on terminals 1 & 2, or if the outdoor temperature exceeds the Warm Weather Shut Down (WWSD) setting.0 -
tekmar 360
You need to contact your local tekmar rep or call tekmar @ 250-545-7749.
Be prepared to explain your wiring and settings. They are only as good as the information you give them.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements