boiler size
captpete12
Member Posts: 11
i have a 12 apts. in one building the boiler is a burnham v 2009a oil fired steam a contractor came out to give me a price on a burnham gas fired k5006 steam boiler. my problem is the oil boiler is 2500 sq. ft. of steam, the new gas unit they want to give me is 1004 sq. ft. of steam someone please help me understand this one. i thought gas was less/ than oil
0
Comments
-
Apples to Oranges,,,
NG is not as hot a flame as oil, so that`s a factor(not in his favor), but
did he perform any kind of H/L for the units as they are now?
Perhaps you don`t need to satisfy HUGE rads completely across all the sections to meet the load requirements nowadays, if it`s an "old system" building upgrades definitely reduce the needed load,,, but again, that can ONLY be calculated by a proper H/Loss room by room.
Tricky stuff if you play-it that way,,,, but it is accurate!0 -
See my answer
in the thread you posted under Strictly Steam.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Good Advice Frank (old friend) ;-),
I keep forgetting about the other WALL categories Dan has,, :-)0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements