Combustion air for power burner?
Patrick_North
Member Posts: 249
Hoping to dramatically tighten up the envelop in my boiler room this summer. Heretofore, a large, leaky barn-door led directly to a (defunct) coal bin under the front porch. I'll also be replacing a woefully inadequate door under our Belco doors.
We recently installed a new steam boiler with a Carlin EZ gas burner. I asked our installer at the time about the effect insulating might have on combustion and his solution was essentially "don't insulate the boiler room."
I wasn't going to try to argue the point. anybody know if there's an aftermarket solution here to supply the power burner with combustion air? The house will be by no means air tight, but I'd rather be safe.
Thanks,
Patrick
We recently installed a new steam boiler with a Carlin EZ gas burner. I asked our installer at the time about the effect insulating might have on combustion and his solution was essentially "don't insulate the boiler room."
I wasn't going to try to argue the point. anybody know if there's an aftermarket solution here to supply the power burner with combustion air? The house will be by no means air tight, but I'd rather be safe.
Thanks,
Patrick
0
Comments
-
There is
it's a "boot" that will fit on the burner's air intake, to which a duct connects going to the outside. That's one of the things we like about the EZ-Gas.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Where is it?
I looked all over Carlin's website and couldn't find anything like this, and I don't seem to be searching for the right thing on the web. Can you point me to this thing?
Thanks,
Patrick0 -
part numbers
Carlin Air boot for Ez Gas burner
Horizontal mount: 97406A
Vertical mount (roof) : 97406B
when in doubt, call the manufacturer.
-
TomMThere was an error rendering this rich post.
0 -
for the record
for the record:
according to NFPA 31
1 cu foot of airspace will support 20 BTUs.
For example:
30'x16'x8' room = 3840 cu feet
3840 cuft x 20 BTU = 76800 BTU
So this room would only support a 76800 appliance if it was completely buttoned up and air tight. (don't forget to adjust for downfiring)
Actually, I can't figure out why intake air boots aren't installed on ALL boiler systems.
Also, efficiency would be improved by using cold air from outside.
screw it, put a supercharger on it.There was an error rendering this rich post.
0 -
That's it!
Thanks!
Patrick0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements