Steam Balancing Protocol
Therm_lag
Member Posts: 30
<a href="file:///C:/Users/John/AppData/Local/Temp/msohtmlclip1/01/clip_filelist.xml"></a><a href="file:///C:/Users/John/AppData/Local/Temp/msohtmlclip1/01/clip_themedata.thmx"></a><a href="file:///C:/Users/John/AppData/Local/Temp/msohtmlclip1/01/clip_colorschememapping.xml"></a>
I have incorporated study results from the Center for Energy and Environment in energy audit work and the small amount of
field installation work I’ve done. MNCEE
(dot ORG) studies include balancing single-pipe steam, boiler vent dampers,
front-end boiler, burner tuning according to a protocol, conversion of steam to
hot water, (and others). George Peterson’s “Achieving Even Space
Heating in Single Pipe Steam Buildings, 1985” can be used almost directly
as a balancing guide and specification. Note
that studies of boiler performance were separate from balancing work, and
Peterson’s work assumes a well-functioning boiler. Peterson’s studies lead him to say (most below is paraphrased or re-stated from 32 pgs):
Steam system fill time is a function of mass of the
distribution system (including radiators) times specific heat (thermal
mass). The main determinant of fill time is the ratio
of the boiler output to the heat capacity of the distribution system.
Fill time for the distribution system is directly related
to initial temperature of the distribution system – cycle needs to be longer in
mild weather,
Further, at
a given pressure the fill time of a radiator varies in proportion to its heat
capacity and in inverse proportion to
the venting capacity of the radiator air vent.
Proper air venting can be used to control the relative
speed of steam delivery to various radiators.
Beyond a certain open area, increased vent orifice size
has little influence on fill time.
Balancing can be achieved by following certain steps:
1) Increase main line venting and restrict steam to
radiators near the boiler (TRVs) as an initial balancing step.
2) Establish cycle length sufficient to fill all
radiators (if possible). Thermostat should have an adjustable dead band,
3) Correct performance problems of radiators (slope,
valve, replace missing, etc.),
4) Reduce operating pressure setting or lower the
temperature in the building until cold discomfort is reported,
5) Increase venting where cold discomfort occurs. Repeat reductions and “up venting” to balance
the building to the extent possible using variable orifice or adjustable
radiator vents.
6) Place TRVs at locations distant from boiler that
overheat, and possibly thermostatic inlet valve for radiators near a brick set
boiler to restrict steam entry on the off-cycle.
7) Though a formatted approach can be used, at a certain
point in fine tuning, steam balancing transitions from “science” to “art”
Space
temperature control is limited to about 4°F
for temperature differences between apartments and swings of temperature within an
apartment. Energy savings of about
10% are seen, although buildings that
have areas not kept at comfort temperatures may actually increase in energy
use.
The original report contains a great deal of detail beyond this quick summary.
I hope to learn if this approach to balancing is
widespread and to hear about different practices and understandings.
mild weather,
Further, at
radiator vents.
Space
use.
Well, first of all
I've never heard of this book. I'd want to read it before speaking to this. Where can I get a copy?
The one thing I'll say now is that converting steam piping and radiators to hot-water can open up some big cans of worms. Our company does not recommend or perform such conversions. We find we can get similar results by fixing steam systems, at considerably less cost and risk.All Steamed Up, Inc.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
Steam balancing
Attached is the article regarding efficiency gained from proper balancing of steam systems. More studies and articles can be found here:
http://www.mncee.org/research/technical_publications/index.php0 -
I thought those articles looked familiar
they formed the basis for the book, "Improving Energy Efficiency in Apartment Buildings", published by ACEEE. Released in 1995, it was likely put together before anyone had ever heard of Dan's "The Lost Art of Steam Heating", so some of the information therein is out of date.
Therm_Lag, the best article I've seen on balancing steam systems is in an e-book you can get here:
http://www.heatinghelp.com/products/Books/5/146/Balancing-Steam-Systems-Using-a-Vent-Capacity-Chart-by-Gerry-Gill-and-Steve-Pajek
Gerry and Steve, through extensive testing of vents and steam traps under controlled conditions, have reduced the selection of air vents to a set of calculations. Once in a while you need to fine-tune the results but their methods at least get you 90% there. The objective is to fill all the mains with steam before starting to heat the radiators- even those close to the boiler. So there shouldn't be any need to over-vent the furthest radiators, which can cause banging on one-pipe systems.
TRVs take control to the next level, letting occupants limit the temperatures in their rooms if they wish.
Besides "Lost Art" and the Gill/Pajek e-book, get a copy of Dan's brand-new book "Greening Steam". It specifically addresses some of the easiest, least costly ways to make steam systems more efficient and more comfortable. They're all in this site's online store- click "Shop" at the top of this page to get there.All Steamed Up, Inc.
- 81.2K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 37 Biomass
- 394 Carbon Monoxide Awareness
- 2.7K Controls
- 1.4K Domestic Hot Water
- 3.8K Gas Heating
- 101 Geothermal
- 133 Indoor-Air Quality
- 2.4K Oil Heating
- 32 Pipe Deterioration
- 581 Plumbing
- 4.3K Radiant Heating
- 334 Solar
- 12.3K Strictly Steam
- 38 Water Quality
- 11 Industry Classes
- 52 Job Opportunities
- 8 Recall Announcements