tekmar 269 question
nicholas bonham-carter
Member Posts: 8,578
the tekmar 269/279 has an indoor temperature sensor, as well as an outdoor temperature sensor. what would the effect of temporarily opening a window [for fresh air] in the area of the indoor sensor?
if i do this with my visionpro thermostat [equipped with a remote sensor] , then the boiler will run because of the lower temperature in the remote sensor area; but maybe the effect would not be the same for the tekmar.
unfortunately, tekmar have no tech support email address that i can find.--nbc
if i do this with my visionpro thermostat [equipped with a remote sensor] , then the boiler will run because of the lower temperature in the remote sensor area; but maybe the effect would not be the same for the tekmar.
unfortunately, tekmar have no tech support email address that i can find.--nbc
0
Comments
-
tekmar 279
Are you opening the window for temporary fresh air or is this an every day thing?
If it's everyday, then you should move the indoor sensor. It's purpose is to provide indoor temperature readings to the control to cycle the boiler.
Tekmar likes for their reps to be first contact with tech service. They do have an excellent tech service dept. You can call them by phone or send a message through their regular e-mail. It will get to the right people.0 -
tekmar steam control and tech support email
First off for tekmar tech support you can email : customerservice@tekmarcontrols.com or call 250-545-7749.
As for the steam control / indoor sensor question: If the indoor sensor sees the room temperature fall below the controls 'Room' setting it will cause the heating curve to be shifted up. In most cases this will cause an increase in the % on-time calculation.
As long as you are not in WWSD.
The control will fire for a longer period in the heat cycle - phase2 . The greater the amount of error the more shift will occur. There is a limit on how much shift is allowed. Usually recommend a heat cycle length of about 60 minutes to give the reset a good opportunity to vary on times.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements