these 2 vents had BURST under pressure...
jpf321
Member Posts: 1,568
At my neighbor's house, they asked me to look at two rads which spewed steam and sounded like a jet engine .. this is what I found...I asked them if they ever went away in winter without leaving the heat on, they said no.
They are stamped USAV .. made in China .. I assume they were bought at big-box-orange store.
<img src="http://lh5.ggpht.com/_JuuICk78iPs/S7ZltiWMzoI/AAAAAAADYW4/SM3ZQ05rWsw/s720/IMG_9648.JPG" width="720" height="481" alt="" />
<img src="http://lh5.ggpht.com/_JuuICk78iPs/S7Zl49hLchI/AAAAAAADYXI/sj5C9nH8SRQ/exploded_vent_2.jpg" width="552" height="476" alt="" />
<img src="http://lh6.ggpht.com/_JuuICk78iPs/S7Zl39tAO_I/AAAAAAADYXA/oRpT-KH-wao/s720/IMG_9650.JPG" width="720" height="481" alt="" />
<img src="http://lh5.ggpht.com/_JuuICk78iPs/S7Zl5RI5hKI/AAAAAAADYXQ/3RYhBFw6ePM/exploded_vent_1.jpg" alt="" />
They are stamped USAV .. made in China .. I assume they were bought at big-box-orange store.
<img src="http://lh5.ggpht.com/_JuuICk78iPs/S7ZltiWMzoI/AAAAAAADYW4/SM3ZQ05rWsw/s720/IMG_9648.JPG" width="720" height="481" alt="" />
<img src="http://lh5.ggpht.com/_JuuICk78iPs/S7Zl49hLchI/AAAAAAADYXI/sj5C9nH8SRQ/exploded_vent_2.jpg" width="552" height="476" alt="" />
<img src="http://lh6.ggpht.com/_JuuICk78iPs/S7Zl39tAO_I/AAAAAAADYXA/oRpT-KH-wao/s720/IMG_9650.JPG" width="720" height="481" alt="" />
<img src="http://lh5.ggpht.com/_JuuICk78iPs/S7Zl5RI5hKI/AAAAAAADYXQ/3RYhBFw6ePM/exploded_vent_1.jpg" alt="" />
1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics
0
Comments
-
Not surprising for that brand
and yes, they are sold at Home Depot.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
a little problem?
even as shoddy a product as they are, what sort of pressure would there have been to have done that?--nbc0 -
pressure unknown .. i'd love to see a test
they are running a Burnham Independence rated for 450sq ft. They only have about 250sq ft installed EDR. These 2 were on the "back main" which is a counter-current main which services 3 rads basically directly overhead of the boiler. The boiler cycled very well ON LOW WATER, not pressure.
Their 0-30psi pressure gauge is basically dead (goes up to 4lbs and stays there until very cooled down) .. I couldnt get the gauge off .. so I left it but installed a 0.0-3psi gauge next to the p-trol. I have a funny feeling that the pigtail was clogged as well.
It's all working well now (except for the 0-30psi gauge) .. there are a few notes about the pressuretrol in another thread I posted earlier today.
if anyone, for the sake of answering NBC's question, wants to get a HD USAV vent and stick it on some regulated heated pressure testing rig, I'd love to hear at what pressure they split.
jpf1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
May not be caused by pressure.
Those vents definitely look to be poor quality, but the split may not be caused by excessive pressure. The shells look to be made of drawn brass, which if not alloyed and made correctly will split spontaneously from internal stresses. The splitting is known as "season cracking" and is fairly common. I have several electrical connector housings of similar size and construction which have split in several places. One of them has actually split in so many places that it looks like the petals of a flower opening. None have ever been under any sort of pressure or stress.
So it is probably another case of "high quality" Chinese manufacturing, rather than the fault of excessive system pressure.0 -
hehe..yup ..i've replaced many of those
exact same brands...been very good for business..like i always tell my customers when i'm replacing those junkie vents, ''what do the chinese know about heating with steam?''gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements