New Hope for Standard Pressuretrol?? (and a warning)

jpf321
jpf321 Member Posts: 1,568
I was working on my neighbors system over the last few days .. I managed to dial in the "standard" pressuretrol to cut-out at 0.8psi and cut-in at 0.1psi .. there is a very small calibration hex-screw inside which I was able to adjust with a needlenose pliers. The screw lives between the see-saw and the diaphram. It is adjustable from above the see-saw. (At least in the unit I had in my hands)



Another thing I learned about the standard pressuretrol .. if you adjust them all the way down .. they effectively "lock-off" .. the adjusting screw puts downward pressure on the spring and in turn depresses the microswitch .. <span style="color:#FF0000">so a word of warning when blindly cranking the pressuretrol all the way down .. you've got to have a little bit of tension on the spring NOT compression. </span>
1-pipe Homeowner - Queens, NYC

NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics

Comments

  • gerry gill
    gerry gill Member Posts: 3,078
    good man..

    i like it when people arn't afraid to 'tweak' things..which model were you working on?
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • jpf321
    jpf321 Member Posts: 1,568
    it was the standard 0.5-9psi

    it was the standard 0.5-9psi grey pressuretrol ... which according to the boiler service tag was installed last June ... it had a microswitch not mercury .. i don't have the exact specs but the 404A type. wait until you see the pictures of the rad vents which "exploded"



    funny thing about the boiler service tag ..

    entry 1 -- chk ok

    entry 2 -- seasonal check ok

    entry 3 -- 6/25/09 -- installed pressuretrol

    entry 4 -- jpf -- 4/2/10 -- cleaned pigtail, calibrated pressuretrol, Ct-Ot=0.8psi Ct-In=0.1psi, inspected LWCO probe, drained + flushed, installed low-pressure-gauge, installed Hoffman 75 main-vent.
    1-pipe Homeowner - Queens, NYC

    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    my NEW system pics | my OLD system pics