Sizing DHW boiler

Timco
Member Posts: 3,040
Laars Mighty Therm just died today, 17+ years old. A replacement is about a week out. I can get a Ajax unit here Tuesday, but the existing boiler is 325K and the Ajax sizes are 300K or 400K. Boiler is heating 3-200gal Lochinvar indirects. Any idea if the 300K unit would do the job? Never sized a DHW boiler before. Ajax for brand? Any thoughts? All 1.25" copper piping.
Tim
Tim
Just a guy running some pipes.
0
Comments
-
What's the load?
laundry? Kitchen? Apartments?
ME0 -
Use
Sorry, apartments. about 40 units.Just a guy running some pipes.0 -
Best bet.
I have always used the RayPak DHW sizing guide. It has never let me down.
It will give you the option of larger boiler, smaller storage, or larger storage, smaller boiler and any combination thereof.
With this tool, you can play the "What if" game and be assured of proper sizing in the end.
You can use their online sizing software called SureSpec at http://www.raypak.com/surespec3.htm
Ajax boilers are a horizontal steel water tube boiler, no?
ME0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 948 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements