Sizing DHW boiler
Timco
Member Posts: 3,040
Laars Mighty Therm just died today, 17+ years old. A replacement is about a week out. I can get a Ajax unit here Tuesday, but the existing boiler is 325K and the Ajax sizes are 300K or 400K. Boiler is heating 3-200gal Lochinvar indirects. Any idea if the 300K unit would do the job? Never sized a DHW boiler before. Ajax for brand? Any thoughts? All 1.25" copper piping.
Tim
Tim
Just a guy running some pipes.
0
Comments
-
What's the load?
laundry? Kitchen? Apartments?
METhere was an error rendering this rich post.
0 -
Use
Sorry, apartments. about 40 units.Just a guy running some pipes.0 -
Best bet.
I have always used the RayPak DHW sizing guide. It has never let me down.
It will give you the option of larger boiler, smaller storage, or larger storage, smaller boiler and any combination thereof.
With this tool, you can play the "What if" game and be assured of proper sizing in the end.
You can use their online sizing software called SureSpec at http://www.raypak.com/surespec3.htm
Ajax boilers are a horizontal steel water tube boiler, no?
METhere was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements