Chimney liner questions
bmac_to
Member Posts: 2
Hello,
Three years ago I replaced a 80 year old oil boiler with a Viessmann
Vitola NG boiler (with a lot of advice from this website). Everything
concerning the boiler has been great. However, the chimney cap
(sometimes called crown) is starting to disintegrate.
Some background info - the chimney is about 10 years old so having the
cap disintegrate is premature. The cap is a precast concrete type.
The current chimney liner is a stainless steel liner that was left over
from the oil boiler - it was quite new and the contractor who installed
the boiler did not feel it was necessary to change it.
I think there are one of two possibilities for this premature failure -
the cap was installed incorrectly (wrong mortar, etc), or it is
directly related to the new boiler. Due to the lower exhaust
temperatures of the new boiler, perhaps condensation could be causing
this problem?
What is everyone's opinion? If it is condensation, whould replacing
the liner help? If so, what type would you recommend? Aluminum?
Insulated stainless? Other?
Thanks.
<a href="http://www.heatinghelp.com/forum-reply/1193332/Chimney-liner-questions">
</a>
Three years ago I replaced a 80 year old oil boiler with a Viessmann
Vitola NG boiler (with a lot of advice from this website). Everything
concerning the boiler has been great. However, the chimney cap
(sometimes called crown) is starting to disintegrate.
Some background info - the chimney is about 10 years old so having the
cap disintegrate is premature. The cap is a precast concrete type.
The current chimney liner is a stainless steel liner that was left over
from the oil boiler - it was quite new and the contractor who installed
the boiler did not feel it was necessary to change it.
I think there are one of two possibilities for this premature failure -
the cap was installed incorrectly (wrong mortar, etc), or it is
directly related to the new boiler. Due to the lower exhaust
temperatures of the new boiler, perhaps condensation could be causing
this problem?
What is everyone's opinion? If it is condensation, whould replacing
the liner help? If so, what type would you recommend? Aluminum?
Insulated stainless? Other?
Thanks.
<a href="http://www.heatinghelp.com/forum-reply/1193332/Chimney-liner-questions">
</a>
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements