Can you connect copper to black pipe?
Hey_Obie
Member Posts: 66
I have an old oil hot water system that I want to modify and break into zones. The whole system is black steel pipe. I bought 4 brass zone valves which I am going to attach to 1 1/4 copper manifold that I need to make.
The question is: 'Is it OK to connect threaded copper to black steel. I was at Home Depot and the guys working there said that over time, they can leak. Their solution was to buy Dielectric couplers.
Should I be concerned?
Thanks,
Obie
The question is: 'Is it OK to connect threaded copper to black steel. I was at Home Depot and the guys working there said that over time, they can leak. Their solution was to buy Dielectric couplers.
Should I be concerned?
Thanks,
Obie
0
Comments
-
You Can
You can connect the two, and will most likely be fine. The possible leaks that the Home Depot guys were talking about come from the two different metals being in contact with each other, which causes corrosion. To be absolutely safe, take their advice and use dialectric couplers, but you'll probably be fine without them.0 -
Pipe Dope?
Is there a pipe dope that would reduce the chance of corrosion between the metals?0 -
Copper to steel.........
I've never had much luck with dialectrics. Use a brass nipple or adapter between the copper and steel and you'll be fine.
Good luck,
JimThere was an error rendering this rich post.
0 -
copper to black pipe
I have seen copper to black pipe installed and they were not leaking yet. I personally always felt it was best to be safe and use a brass coupler. Better to be safe and do it once than have to worry that you left a problem on a job to be fixed by another.
I used dielectric unions for a while and had problems getting them to seal. They always seemed to like to come loose and weep or corrode. Brass there is no questions, it done.0 -
Brass is golden
Brass it is. Thanks guys0 -
Not a problem
We transition from black steel to copper on every job ( hot water , closed systems ) , using the basic copper to male or copper to female adapters .
We also remove the old equipment that had the same transitions for decades . Never see leaks at these adapters or any dielectric buildup whatsoever .
We do from time to time see leaks due to the fitting not being tight enough or not enough thread sealant . Which is why we solder a small piece of copper into the adapter then retighten while it's still hot .0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements