I have four zone valves on my 4 zone hot water boiler, with a 40 volt transformer. one zone was added and the valves have been erratic ever since. I have read somewhere, that 3 taco valves are the max that should be on a system with a 40 volt transformer. Is this true?
0
Comments
-
I assume....
....we are working with the 570 series Taco ZV? And that they are wired direct to the thermostat without a relay (i.e. ZVC404)? Has anything else changed besides just adding a zone (new thermostats)? Have the thermostat anticipators been matched to the 570 amp draw? Sorry for all the questions, but I don't know what eratic you are referring to. Theoretically, the valves could be pulling 96 VA if they are all trying to open simultaneously, which almost never happens.
Direct wired, I prefer a 50 VA for 4 valves, but in the ZVC404 relay there is a 40 VA for 4 valves. I believe that is due to the way the circuit board handles the draw.There was an error rendering this rich post.
0 -
570's
Yes they are 570's and they are wired direct direct to the thermos. I have to confess I don't know what a thermostat anticipator is. Somtimes a valve will not open when when the thermostat is turned up if I push the valve to manual then back to auto it will work. It is not always the same valve. All of the heads have been changed. I still have the problem occasionally.0 -
The thermostat......
.... can make a big difference. If they Honeywell T-87 (round, mercury tube) the anticpator is inside. Pull the outer ring and it's on the bottom of the stat. The dial has numbers and the pointer should be to the left at .9 or 1.0.
If it a digital thermostat, make sure it is battery powered and doesn't rely on 24 volts for it's power (unless there is a resistor across terminals 1 & 2 of the zone valve.
A 40 VA transformer could be the issue, especially if it has some age on it. A 50 VA transformer would be better..There was an error rendering this rich post.
0 -
Anticipators
The anticpators were not in the position that you said they should be . I moved them there and am ordering a 50 volt transformer. Iwill see if that helps.
Thank you0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements