Steam main reduced
Steve_210
Member Posts: 647
I just looked at a job where the boiler was moved from the middle of the building to the front of the building. The 1 steam main run's from the front to the rear, originally it was 2 1/2" problem is that the guy who relocated the boiler extended the main to the front possibly about 8ft in 2". Therefore the main starts off in 2" and then increases to 2 1/2". I know this is totally wrong but I am trying to figure out the full consequences in doing this. I have laosh and I have all the charts to size the main properly, I'm just trying to figure out the full consequences of reducing the main where the guy did this. The house has a lot of uneven heat problems, though the main is vented with 1 Gorton No: 2 and the boiler water is clean and neutral.I am really just trying to figure out how much of the problem I will solve by putting the main back to its original size. The combined 2" & 2 1/2" main is approximately 35ft long.
0
Comments
-
How much radiation
is on that main?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
32080 btu;s
even with a 50% pick up it should be well within the 92640btu,s0 -
Only 134 square feet EDR?
2" is plenty. Wonder why the original is 2-1/2?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
all rads replaced
with governale convectors. the originals were proubly alot larger??
gut renovation done 6-7 years ago0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements