Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Steam main reduced

Steve_210
Steve_210 Member Posts: 647
I just looked at a job where the boiler was moved from the middle of the building to the front of the building. The 1 steam main run's from the front to the rear, originally it was 2 1/2"  problem is that the guy who relocated the boiler extended the main to the front possibly about 8ft in 2". Therefore the main starts off in 2" and then increases to 2 1/2". I know this is totally wrong but I am trying to figure out the full consequences in doing this. I have laosh and I have all the charts to size the main properly, I'm just trying to figure out the full consequences of reducing the main where the guy did this. The house has a lot of uneven heat problems, though the main is vented with 1 Gorton No: 2 and the boiler water is clean and neutral.I am really just trying to figure out how much of the problem I will solve by putting the main back to its original size. The combined 2" & 2 1/2" main is approximately 35ft long.

Comments

  • Steamhead
    Steamhead Member Posts: 17,380
    How much radiation

    is on that main? 
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Steve_210
    Steve_210 Member Posts: 647
    32080 btu;s

    even with a 50% pick up it should be well within the 92640btu,s
  • Steamhead
    Steamhead Member Posts: 17,380
    Only 134 square feet EDR?

    2" is plenty. Wonder why the original is 2-1/2? 
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Steve_210
    Steve_210 Member Posts: 647
    all rads replaced

    with governale convectors. the originals were proubly alot larger??

    gut renovation done 6-7 years ago
This discussion has been closed.