Carlin 41000 premature failure
shoudabeenaplumba
Member Posts: 74
in Oil Heating
What are some of the causes for an igniter to fail prematurely? I'm working on a Beckett AF burner. Date code '94. Everything else seems to be original and functioning correctly, but the igniter is dated Feb, 06 and is giving no spark even when control is bypassed, leading me to believe this transformer is dead.
0
Comments
-
I have....
I have seen them fail in a year I have seen them last 10 plus. Check for good grounding, proper input voltage, and good wiring connections. Also make sure that the lock washer was installed on the screw between the ignitor and the mounting plate. It also must be in the screw hole with the metal bar connected to it, this is for the ground. I usually scrape some of the paint away. Sounds like your current ignitor is bad, when you replace it do the items listed and you should have better results.0 -
Really frustrating
I don't deal with HV transformers, usually the other direction for me. After about dozen lockouts sprinkled over the course of three weeks, I finally got around to shaking/breaking a real problem out of it.0 -
toilburn
Electronic ignitors don't last long if they are connected to a contol that keeps the ignitor on thru the entire run cycle. That being said, I found that Carlin ignitors seem to fail more often. I have switched to Becketts line of ignitors with a little better results. The best thing to do is switch control to a Honeywell 7184U or a Beckett Genysis0 -
Control says intermittant
Honeywell R8184g. I don't know if supposed shut off, but I know the head will stay lit if the igniter is lifted away. That's what threw me, because I was getting very good spark-when I got it. I figured it was air bubbles or dirty flues or dirty filters or bad pressure or partially plugged line. It took 2 hours sitting on a bucket reading a book to reall start to figure out what was going on. I replaced it and haven't had a problem today.
I only have to make it 2 months. Of course, my new burner will be a Riello so the learning will start all over again!0 -
I have gone back to......
.... standard ignition transformers. I have replaced 7 electronic ignitors this year alone. Doesn't matter if it is interupted or intermittent ignition. The electronic versions just don't hold up. I like service, but not silly service.
Riello has had electronic ignitors for ever and I have only replaced one in the decade.There was an error rendering this rich post.
0 -
riello
The reason the Riello lasts is it is only on for 1 or 2 seconds at light off0 -
interrupted ignition
is what will make those last. Also testing them is critical. The old screwdriver test will kill them if you dead short the srings to draw a spark. They are also not mid-point ground as the old tar ones, and need to be wired hot to hot, ground to ground. I have seen a few failures also, but only those with intermittant ignition. peace0 -
interrupted ignition
reposted0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements