Pressure relief valve

Luv'nsteam
Luv'nsteam Member Posts: 278
I am installing a Peerless WBV-03 steam boiler.  Peerless recommends placing the relief valve on top of the boiler, near the riser.  They provide an alternate location at the rear of the boiler.  This second spot is dead-level with the skim port.  I would like to use the rear location for ease of attaching a pipe to the relief valve leading to the floor.  How far above the hole should I place the relief valve (ie: how long of a nipple should I use)?



Thank you,



Mike

Comments

  • Chris M_2
    Chris M_2 Member Posts: 67
    Pressure Relief Valve

    The length of the nipple doesn't really matter, but for practical purposes, the pressure relief valve itself should be located as close to the boiler as possible (that's where it's doing it's job) while also being easily accessible for periodic blowdown or replacement.
  • Luv'nsteam
    Luv'nsteam Member Posts: 278
    Relief valve location

    Thank you Chris.  I will keep it close to the boiler.



    Mike