NOS mercury vaporstat is garbage...
tmw
Member Posts: 56
I have a NOS honeywell 0-16 oz (probably the last version of the mercury style before the microswitch) which is completely innacurate. I read Mr. Gill's thread and plan to build his testing rig.
Problem is no easy way to adjust this model. Only way I can think of is to pull the spring out and fool with it until I get the proper tension.
Has anyone done this?
Problem is no easy way to adjust this model. Only way I can think of is to pull the spring out and fool with it until I get the proper tension.
Has anyone done this?
0
Comments
-
Is it possible
the scale is out of adjustment? Some of these have scales that you can slide after loosening two screws......All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I wish it were the scale..
It's unfortunately the spring.I have to take it out and try to stretch it a bit, then hope for the best. absurd0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements