steam header question

This steam header comes up then turns around the flue pipe<span style="text-decoration:underline;">.which</span> horizontal pipe or header

needs to be 24" above waterline??There is 3 horizontal sections,last el is cut off in picture.The equalizer is tough to see in this pic,but its in the vertical section between the 2nd and 3rd elbow.Its undersized at 1".I know the piping should not be copper,and insulated-it was put in by others.

Comments

  • Steamhead
    Steamhead Member Posts: 17,380
    The first horizontal pipe

    needs to be 24" above the highest possible waterline. You probably don't have the required height, which is one of many reasons to have it redone correctly. 



    What make and model boiler is that?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • JStar
    JStar Member Posts: 2,752
    edited March 2010
    Wow.

    I only have one question....How many problems do you have in this system? Water hammer, spitting vents, uneven heating, water surging.....
  • luckyloser
    luckyloser Member Posts: 5
    e

    I Dont remember the brand ,approx 91,000 BTU - 283 sq ft EDR,and surprisingly no surging waterline,no spitting,some minor hammer on cold start.
  • gerry gill
    gerry gill Member Posts: 3,078
    YUK!!!!!!

    if i did that it wouldn't work at all..go figure.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • JStar
    JStar Member Posts: 2,752
    Hahaha

    It would be 8 o'clock at night, every vent would be spitting water, mains hammering like a steel mill, and enough surging in the glass to make you slowly back out of the boiler room and run to your truck.