I am replacing all of the wet returns. Use black or galvanized pipe? Advantage of one over the other?
Thank you,
Mike
Thank you,
Mike
0
Comments
-
black
galvanized flakesCost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Black pipe
Noted, Charlie.
Thank you,
Mike0 -
feed water connection
while you are re-piping, why not leave provision for flushing out with well-placed full-port ball valves, usually placed at the lowest points in the wet returns.
in addition, the feed water connection is best connected into the return, with as much distance as possible between it and the boiler [so as to mix the cooler fresh with the warm return water].--nbc0 -
feed water
Nick, if my chicken-scratch diagram of near-boiler piping is legible, you can see the feed water is supplied between the wet return and the Hartford loop. There is also a water meter with bypass valves, as well. The water in my town is excessively hard with calcium & magnesium, so I will be feeding water to the boiler from my water heater. This way, most of the hard minerals will fall out of suspension in the water heater and not the boiler & of course, the water will already be hot. I already drain my water heater every eight months or so and a water heater is far less expensive and easier to replace then the boiler. Your thoughts?
Thank you,
Mike0 -
Copper?
I've seen quite a few recommendations for copper .. but only below the water line, nowhere that will be in contact with steam. Any thoughts from a pro on this?0 -
Copper returns,
I'm fairly sure, are not the best choice for steam applications. I have seen them used many times, but somewhere in TLAOSH, Dan points out that the copper can leach (correct word?) off of the inside of the copper pipe, get into the boiler with the water and corrode or cause corrosion when in contact with the boiler metal. My feed water supply will be copper but I will use a transition adapter to bring it into the wet return via a cast iron tee. From there it will likely all be black pipe.
Any pro's want to comment on using copper in a steam plant?
Thank you,
Mike0 -
way back in Nov
i asked the same questions ... regarding returns .. you maybe able to find the thread if you search both cooper and galvanized perhaps .. copper was the strong contender. and I have seen many "pro" pictures where copper is used for returns I think.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
wet returns
That's what I remember too. I thought a couple of the pros said that copper is actually good for wet returns, but wet returns and water supplies were the only place that there should be copper in a steam system .. no steam-copper contact.0 -
wet returns
I believe I am going to stick with black pipe. To all who responded,
Thank you,
Mike0 -
If steel.....
you may want to go to Schedule 80. The walls are alot thicker so it sould have a much longer life.There was an error rendering this rich post.
0 -
schedule 80
is thicker than schedule 40? What is the typical pipe at say, Depot or Lowe's? How much of a difference between the two? Thanks for the recommendation, information and suggestion.
All the best,
Mike0 -
More than you'd ever want to know…
about schedule 40 and 80 steel pipe at:
http://www.engineeringtoolbox.com/ansi-steel-pipes-d_305.html
http://www.engineeringtoolbox.com/ansi-steel-pipes-d_306.htmlThere was an error rendering this rich post.
0 -
Scheduled pipe thickness
Brian, thanks for the links. I see schedule 80 is, on average, about 25% thicker than schedule 40 pipe. I will definitely aim for schedule 80 in black. I will also save those links for further reference
Thank you,
Mike0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements