BTUs for this radiator?

Hi folks:



Can anyone help me determine the BTUs for this radiator?  it is 30 inches high, 30 inches wide, and 24 inches deep.



It says USRADCORP on the side.



Any help would be appreciated!



Patrick

Comments

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,594
    It would be 35 square feet EDR

    That's what they show for their Capitol, four-tube radiator, although that's for one 32" high (there's no 30"-high model) Are you measuring from the floor?
    Retired and loving it.
  • Steamhead
    Steamhead Member Posts: 17,312
    That's a 4-column radiator

    closest I can find is 65 square feet, which is for a 32-inch rad- maybe someone cut the legs off shorter? 
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • FJL
    FJL Member Posts: 354
    edited March 2010
    Capitol Rads

    Here is the link of the numbers for Captiol Rads from the Library here.  It gives you the different measurements for the rads:  http://www.heatinghelp.com/article/158/Radiators/1281/U-S-Capitol-Radiators

    You will need to download the PDF and turn to the page with 4-tube rads.
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,594
    Big difference from what I'm showing.

    ???
    Retired and loving it.
  • Patrick McGrath
    Patrick McGrath Member Posts: 59
    It was in the snow!

    So, it very much could be 32".  I was freezing to death measuring it.  The snow was hard packed, so my tape may not have gone all the way to the ground.



    I am in need of a 10-12,000 BTU rad.  What is the square foot to BTU conversion formula?



    Thanks all for the quick responses (and Dan himself!  Rarified air!).



    Patrick
  • Steamhead
    Steamhead Member Posts: 17,312
    edited March 2010
    On steam

    this rad will produce 15,600 BTUH. On hot water with boiler water at 180 and a 20°  ΔT it will produce 9750 BTUH.



    The slightly rounded top and thick outer vertical members of each section ID this as a column rad rather than a tube type. Also it is much deeper, front-to-back, than a 4-tube rad, and I'll bet it has a 3-inch section spacing rather than the more-usual 2-1/2". Look at the PDF file that FJL mentioned, with its pics and dimensions of tube rads, and you'll see the difference.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Patrick McGrath
    Patrick McGrath Member Posts: 59
    edited February 2011
    Thanks!

    Thanks Steamhead!  That is good help.



    My radiant heat specialist did a heat loss calculation on my house, and I found a room that was under-radiated.  He informed me that the line to that spot can handle up to 13,000 BTUs, so I assume this one won't work out for me.



    I attached the heat loss calculations (I did this for another post, so I hope I am not bothering you guys).  The room in question is "Katie's".



    I am overshooting her room needs - I'd rather have more than less in this room, and I figure that I can slow down the rad with venting if it's too warm in there.  This room faces the wind and has really big windows in it.  We just had the house insulated, which helped a bit.  The rad in her room is double vented right now with Gorton Ds, so I really can't pull any more heat from it.  I tried a Heatimer Varivalve, too.



    Thanks again for your help!
  • Steamhead
    Steamhead Member Posts: 17,312
    What size

    is the pipe that leads from the main to the rad? 
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Patrick McGrath
    Patrick McGrath Member Posts: 59
    pipe size

    Steamhead - the valve coming into the rad is 1 1/4".  Is that what you mean?

    I can take a pic of it tomorrow night if need be.