0 smoke
G Waite
Member Posts: 23
Still very new. I was cleaning my furnace today. I replaced my tank filter, checked my screener, and cleaned assembly, changed nozzle. unit calls for .75 70 A I had a .75 80B so I used it. I also noticed that the end cone was loose on the very end I had the burner out. I put it all back togather and fired her she looked nice. I just couldnt get a 0 smoke. I also checked pump pressure with guages 100psi and nice cut off also held pressure. Why no 0 smoke?
0
Comments
-
Change it back..........
...to a 70° A.There was an error rendering this rich post.
0 -
0 smoke
Thank you.0 -
That B nozzle
produces a longer flame pattern than the A, and it's probably either a poor match for the air pattern of your unit, or it's hitting the target wall at the back of the firing zone. The latter will chill the flame and generate smoke. The flame temperature is important- if it's too low, you won't get complete combustion.
A modern oil burner should produce good combustion efficiency with no smoke whatsoever. If it does make smoke, something is wrong.
What model boiler and burner do you have? What test equipment are you using? What were the numbers for CO, CO2, stack temp etc?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements