what is the flow rate for half inch pex when applied to a conventional boiler with convectors
0
Comments
-
It depends....
on NUMEROUS variables, like pump size and pipe length.
A general guide is to limit the flow in a 1/2" pipe to less than 2 GPM, preferably more like 1.5 GPM.
At a 20 degree F differential in temperature, that flow would deliver 15,000 btuH to a properly sized heat emitter.