Honeywell Tru Steam ???
Steve Ebels_3
Member Posts: 1,291
I'm trying to install one for a customer with an old oil furnace.
Knowing that the furnace has no fan control except the fan/limit, I
specifically asked the distributor if the humidifier had relays to make
the blower function correctly. They said if I bought the humidifier
that came as a kit with the equipment interface module I would have
everything I need to make it work.................Right............
So, I've been through all the tech guys at the distributor plus two
different people in Honeywell "tech" service and they haven't been able
to give an answer as to how to wire this thing up. It appears that i
will have to field engineer it myself but I can't even get a straight
answer from Honeywell regarding what terminals are powered and what
ones are dry contacts. Different answers to that question from two
different Honeywell personnel. Getting a little frustrated and so is my
customer.
Anyone worked with one of these and integrated it into a system lacking normal R,W,Y.G,C contacts ?
Anyone know of a particular person I could ask for at Honeywell that actually knows what they are talking about?
Posted on the Main Wall also
Knowing that the furnace has no fan control except the fan/limit, I
specifically asked the distributor if the humidifier had relays to make
the blower function correctly. They said if I bought the humidifier
that came as a kit with the equipment interface module I would have
everything I need to make it work.................Right............
So, I've been through all the tech guys at the distributor plus two
different people in Honeywell "tech" service and they haven't been able
to give an answer as to how to wire this thing up. It appears that i
will have to field engineer it myself but I can't even get a straight
answer from Honeywell regarding what terminals are powered and what
ones are dry contacts. Different answers to that question from two
different Honeywell personnel. Getting a little frustrated and so is my
customer.
Anyone worked with one of these and integrated it into a system lacking normal R,W,Y.G,C contacts ?
Anyone know of a particular person I could ask for at Honeywell that actually knows what they are talking about?
Posted on the Main Wall also
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements