gravity hot water conversion
Brian Maffioli_2
Member Posts: 13
I have been reading and trying to educate myself about a gravity hot water system conversion I just looked at today. I am pretty confident about the whole process except for the reducing of the near boiler piping.
What constitutes near boiler piping? There is what appears to be a 3 inch supply main that travels at least 10-15 feet from the boiler with some parts hiding inside of a soffit of a finished basement.
How near is near boiler piping?
Thanks in advance.
What constitutes near boiler piping? There is what appears to be a 3 inch supply main that travels at least 10-15 feet from the boiler with some parts hiding inside of a soffit of a finished basement.
How near is near boiler piping?
Thanks in advance.
0
Comments
-
That piping which is connected TO the boiler...
is NEAR boiler piping.
Rule of thumb, 1/2 of that piping, then one pipe size less, so in your case, 1-1/4" new near boiler piping.
METhere was an error rendering this rich post.
0 -
gravity
Hi Mark,
So if I understand this right, if my 3 inch supply main starts at the boiler and continues 10-15 feet away from the boiler, that whole length is considered "near boiler piping?"0 -
Correct
If you wanted to break the pipe back to the first branch, and install a 3" X 1-1/4" bushing, that would be acceptable.
METhere was an error rendering this rich post.
0 -
Gravity conversion
Remember, your gravity system is a 2 pipe direct return. When you add a pump the water is going to take the path of least resistance. Reverse the returns or add TRV,s to retain some balance in the system.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements