150 controller and short cycling
tom_82
Member Posts: 66
We have a large one pipe steam system.
we have installed several new vents throughout the system and things were running...ok.
We started to have a short cycling, the water gauge glass was filthy and overflowing. I think some of the vents are no longer working, for they just spit and gurggle while under pressure.
We called our oil company and they came out and made a call.
THis is what they fixed.
Does it sound appropriate?
"This(short cycling) was being caused by the 150 pump
controller. To correct this issue our technician throttled the ball
valve on the make up tank to create enough head pressure to the
boiler. He also adjusted the differential on the 150 pump controller
to alleviate the short cycling.
T
T
Post your question in the "Strictly Steam" forum. You may get more replies if you re-word your query to be less confrontational, i.e. leave out the oil company.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
- 120 Geothermal
- 394 Solar
