Water dripping from steam pipe
Joe123
Member Posts: 4
I'm new here. I had a power problem last night. Lights flickered for a couple of hours (problem was a faulty transformer outside) during which I heard knocking in my steam pipes. Then the pipe closest to the furnace started to leak water through the ceiling sheetrock in the basement. Could be coincidence but I'm assuming everything is related. I was hoping it would stop when the power was restored to normal but it didn't. I never had a problem with the steam pipes before. Any advice would be greatly appreciated.
0
Comments
-
Water leak?
I'm afraid I can't think of a way that steam and electricity would be related to cause a leak. I would suggest that it has something to do with a waterline. Is there a waterline in the general vicinity of the leak? Possibly the electrical problem caused a valve to shut down suddenly and the resulting water hammer popped a joint somewhere on the line. The valve doesn't necessarily be close to the leak.
Off hand the only electric valves I can think of might be a dish washer or washing machine or possibly the automatic water unit (if you have one) for the steam boiler. Was any of those operating at the time of the power problems? If you can isolate different branches of the house water system that might be a place to start or perhaps cut a small hole in the ceiling and poke a mirror and a flashlight up there and take a look. Let us know what you find.
- Rod0 -
auto-feeder related?
This is a super long shot, but what would happen if the power went out while the auto-feeder was adding water? Could it get stuck open? (This might be a really stupid idea. I'd be the first to admit that I don't know how the autofeeders work.) It could then flood the system, forcing water upstairs until it found a way out.There was an error rendering this rich post.
0 -
electricity and autofeeder
brian reminded me of Mr. gills article, good thought brian!! .. http://www.gwgillplumbingandheating.com/webapp/GetPage?pid=5001-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
Was the leak
from an actual pipe, or an air vent installed on the pipe?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
evil power
could be that the faulty transformer has fried some part of the auto-fill. if you turn it off, then you could see.--nbc0 -
Thanks JPF
But I think it might be more a case of even a broken clock tells the right time twice a day. Thanks for the link to the article. It made me feel better about not having an autofeeder. Glad there's a way to correct the problem, too.There was an error rendering this rich post.
0 -
Water dripping from steam pipe
The autofeeder article was great, and I'm guessing that is exactly what happened. Any way to check to make sure? If so, what has to be done to repair the problem?
Thanks to all for your help. What a fantastic group of helpful people.0 -
Not sure
Its concealed but I don't believe there are any vents there.0 -
welll ...
if your auto-feeder went crazy .. you should have a completely full glass gauge .. if your glass gauge level looks normal, then it may not be the feeder...1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
But check it when it's cold
JFP had a very good idea about checking the sight glass. I wouldn't have thought of it. But now that he's mentioned it, I'd like to add two thoughts. First, the system may have purged itself of enough water that your gauge won't be completely full. Second, try to check it when the system is as cold as possible. I like to check my the instant the thermostat clicks on since that's the maximal off time for that cycle.There was an error rendering this rich post.
0 -
Bingo!
It's completely full! Now what?0 -
drain to normal level
firstly .. drain, drain drain ... until autofeed kicks in so that you can test that it is filling properly .. and shutting off properly .. after the autofeeder shuts off, then watch your gauge over the next few hours to make sure that no additional water was added due to a leaking auto-feeder ... that *should*solve your drip assuming the drip was caused by a flooded system ... and you should be good to go... i'd also believe that you have had not significant heat since the auto-feeder overfilled your system.
lastly .. once the autofeeder adds the proper amount of water and shutsdown .. make sure you make steam immediately thereafter for about 15-20mins to drive off rust causing dissolved oxygen in the new feed water ..1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements