gauge?
steam83
Member Posts: 19
the gauge that is on my gas fired boiler does not read anything its always 0 what can this mean
0
Comments
-
It could mean…
1. The gauge is broken,
2. The pigtail is clogged,
3. The pressure is too low for the gauge to read. This is good. Many of us have added a gauge with a lower range (say 0-24 or 36 ounces/sq. inch).There was an error rendering this rich post.
0