sizing monoflo
RMA
Member Posts: 55
OK, existing radiators to remain equals 50,500 btu's. existing 32 gpm circulator, 344 mbh boiler,
at 50,500 btu's I think i need a 5gpm circ (10,000 btu's per 1gpm)
what diameter main for a monoflo loop w/ split return?
1" will provide 8 gpm or 80,000 btu's
I am thinking 1" loop with 3/4 branches to the rads.
any comments?
at 50,500 btu's I think i need a 5gpm circ (10,000 btu's per 1gpm)
what diameter main for a monoflo loop w/ split return?
1" will provide 8 gpm or 80,000 btu's
I am thinking 1" loop with 3/4 branches to the rads.
any comments?
0
Comments
-
This is from the Library.
http://www.heatinghelp.com/files/articles/955/281.pdf
Scroll down a few pages to the Monoflo sizing instructions.Retired and loving it.0 -
English
You're kidding me!
Think i'll put a wood stove in instead!0 -
Hey,,, its easy,,,
it is in English,,,, and all right-there in B&W!!!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements