steamhead: help with Megasteam Sizing...
jpf321
Member Posts: 1,568
OK since I'm no longer concerned much with a gas conversion, I'm looking strongly at the Burnham Megasteam .. however, I need a bit of help with sizing ..
I currenlty have 384sq ft of EDR, mains are fully insulated with 1" and PVC jackets/inserts on the fittings.
I have 2 mains, each 2" which branch from boiler and join together at the far end to a wet return making a big loop .. 1 main is 65ft@2" the other is 55ft@2" .. therefore, I don't think I need to worry much about extra P/U factor.
I would like to use the boiler to make DHW .. whether it be by indirect or by tankless coil .. however, I've heard that a tankless coil could really collapse my steam in the boiler ..
I have an empty Electric HW heater/tank next to the boiler currently and would like to use that if I can as an indirect (although I'm not exactly sure how.. but that's for another discussion) ..
So the crux of my problem .. the Megasteam comes in either a 396sq ft or the next size up is 513sq ft .. the 513 seems quite a bit bigger than I need .. and the 396 seems just border line.
And then how best to make my DHW using the boiler... Tankless Coil or Indirect? and does a Tankless Coil significantly affect steam production?
thanks!
I currenlty have 384sq ft of EDR, mains are fully insulated with 1" and PVC jackets/inserts on the fittings.
I have 2 mains, each 2" which branch from boiler and join together at the far end to a wet return making a big loop .. 1 main is 65ft@2" the other is 55ft@2" .. therefore, I don't think I need to worry much about extra P/U factor.
I would like to use the boiler to make DHW .. whether it be by indirect or by tankless coil .. however, I've heard that a tankless coil could really collapse my steam in the boiler ..
I have an empty Electric HW heater/tank next to the boiler currently and would like to use that if I can as an indirect (although I'm not exactly sure how.. but that's for another discussion) ..
So the crux of my problem .. the Megasteam comes in either a 396sq ft or the next size up is 513sq ft .. the 513 seems quite a bit bigger than I need .. and the 396 seems just border line.
And then how best to make my DHW using the boiler... Tankless Coil or Indirect? and does a Tankless Coil significantly affect steam production?
thanks!
1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics
0
Comments
-
First things first-
Assuming you've already tightened up your envelop, you may find that you can lower your attached EDR and still match heatloss. I spent almost two years juggling, removing, and replacing rads prior to our boiler replacement. Connected radiation is still ample (and even), though I lowered the EDR by over 200.
Also, much has been written here lately on effective, intentional undersizing of steam boilers. I believe this is mentioned in Dan's new book, too?
Good luck,
Patrick0 -
good point
Thanks Patrick -- good point .. i will probably tighten my envelope within the coming seasons .. so it may be the case that I will be able to reduce the connected load. Unless anyone yells and shouts, I will likely lean towards the 396 rated unit.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
Go with the 396
it has plenty of capacity for what you want to do. I'd use an indirect rather than a tankless, but your existing tank can be used for increased storage.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
thanks ..
thanks for the sizing help! i've been told that i can't use the empty tank for storage since it needs to have taps for recirc. i may look at the alliance SL for indirect regardless .. i'm not married to this empty tank.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements