HOOK UP #67 LOW WATER CUT OFF

GILL
GILL Member Posts: 1
I AM REPLACING LOW WATER CUT OFF (#67) TO STEAM BOILER WHICH HAS A RELAY #RP 400 .I COULD HOOK UP THE LWC TO 120V FEED, BUT NEED HELP TO MAKE IT CUT OFF BOILER AT LOW WATER.............THANK U...GILL

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 3,020
    LWCO

    A steam boiler electrical runs in series. Not sure voltage of boiler wired. But you can wire #67 line voltage to shut down any just about any unit other then a millivolt gas system. I will wire it line voltage to control the feeder.. With a millivolt system ..Then it will be duel voltage to control the feeder and gas burner. The top two terminals are for the burner. The bottom two are for the feeder. There is a jumper Chanel to bring the line down to the feed switch .. The load will be the other terminals..