Drip question
Johnny13
Member Posts: 45
The pipe coming down from the valve where I do my weekly gunk removal has started to drip. Not terribly, maybe 5 times an hour. Over the course of a week this adds up to about two inches of water in a 5 gallon bucket that I keep under the pipe. When I moved in, there used to be a metal cap on the end of that pipe, and I would take it off when I did the cleaning. Water would come out, but not very much. After I had the boiler serviced this year, the cap disappeared. Was it bad to have it on there? Is it a bad sign that I am losing that much water?
Also, the water level in the glass tube is consistently lower than it was before. It is always about 3" about the marked minimum water level, but about an inch and a half below the old regular level. I turned down the pressure this year, which I only mention in case that could be relevant.
Thank you for your time.
Also, the water level in the glass tube is consistently lower than it was before. It is always about 3" about the marked minimum water level, but about an inch and a half below the old regular level. I turned down the pressure this year, which I only mention in case that could be relevant.
Thank you for your time.
0
Comments
-
leaking valve
are you referring to the blow-down valve of the LWCO on a steam system [go to the head of the class for blowing it down weekly!]? if so, that valve is a replaceable item, from mcdonell-miller; however a partial boiler drain down would be required, so it would be best to have the part in hand, before starting the work. this would be best done by a pro, but you could save him time by having the part there for him. i think the model number is #67, but double check on the M-M website. a rebuilding kit is probably available for the whole thing, and it would be wise to renew all the replaceable parts in it, as it is so important.--nbc0 -
have a look at
have a look at the parts sheet posted in my link here:
http://www.heatinghelp.com/forum-thread/129681/why-we-blowdown-the-LWCO#p11878891-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
Part number
for the blow-down is 14-B. This is the ball-valve type of bleeder. Avoid the older poppet-valve type which is the plain #14.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements