2 pipe steam with F/T's and hoffman 75 main line vents.
Scott McGuire
Member Posts: 21
I worked on a job today in a warehouse with a zoned steam heating system. We have radiators that are downfeed from a main above, then each radiator has a steam trap and drains to a return line to a condensate pump.
The two floors above have ceiling mounted steam blowers. each blower is feed with its own branch and the return goes through a F/T trap and drains to a common return which goes to a condensate tank.
The end of each zoned steam main has an F/T which drains to a common return and then to a condensate tank.
At the end of each steam main is a Hoffman 75 main line vent before the F/T.
The common return lines also have a Hoffman 75 vent on them prior to dropping to the condensate tank.
My question is are the Hoffman 75 vents even needed. (I don't think so.). Since all the returns drain to a vented to the atmosphere condensate tank. These vents are loud when they vent and spit out water at times.
I can see leaving the vent on the return main after the F/T before in drains to the condensate tank to vent the air before it drops to the tank. But the other vents at the ends of the steam mains and prior to the F/T at the end of the main make no sense.
Looking for any insight on this.
Scott
The two floors above have ceiling mounted steam blowers. each blower is feed with its own branch and the return goes through a F/T trap and drains to a common return which goes to a condensate tank.
The end of each zoned steam main has an F/T which drains to a common return and then to a condensate tank.
At the end of each steam main is a Hoffman 75 main line vent before the F/T.
The common return lines also have a Hoffman 75 vent on them prior to dropping to the condensate tank.
My question is are the Hoffman 75 vents even needed. (I don't think so.). Since all the returns drain to a vented to the atmosphere condensate tank. These vents are loud when they vent and spit out water at times.
I can see leaving the vent on the return main after the F/T before in drains to the condensate tank to vent the air before it drops to the tank. But the other vents at the ends of the steam mains and prior to the F/T at the end of the main make no sense.
Looking for any insight on this.
Scott
0
Comments
-
The vent you might not need
is the one on the return before it drops to the tank. If the return goes into the tank without forming a water seal, the vent on the tank will vent the return.
As for the others- keep them. The faster the system vents, the faster it will heat up, and the less fuel it will use.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
The need for vents
What seems to be a very little known is that most F&T traps have very little air venting capacity so when venting mains they rarely have even close to the capacity needed to vent quickly. A quick walk through Gerry and Steve's newer vent tables demonstates this problem. If the vent are making a lot of noise and spitting, you probably need alot more venting capacity, or a much lower capacity boiler.
BoilerproThere was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements