Watts 9d backflow preventer
cowie_4
Member Posts: 18
Why does the vent on a Watts 911D drip water?? I was told that you could put a plug into it if it was on well water. Is this true??
Thanks,
Jay
Thanks,
Jay
0
Comments
-
Don`t plug-it,,,
then you`re just defeating its purpose of being there in the first place.
Just install a small ½" swing check upstream of-it and you should be OK. :-)0 -
More than one reason likely
The vent can expel water for more than one reason, check the tech documents on their site for list of reasons.
If it has been in service for a while the most common reason would be the spring or gasket has something on the face and is not making a positive seal.
Do not plug it, it is telling you something is wrong....fix it. Not sure what a check valve would do?There was an error rendering this rich post.
0 -
Check valve...
installed on the inlet to the backflow preventer will keep the device from seeing any nuisance pressure drops created by high demand fixtures on the potable water system (solenoid controlled devices and flushometers).
Perfectly acceptable. Honestly, I don't know why the manufacturers don't just include on in the assembly in the first place...
METhere was an error rendering this rich post.
0 -
dripping 9D
Might be doing what it is supposed to do or it may need rebuilding but as Mark says, don't plug it......make sure you pipe that vent to a safe place or a suitable drain. I have investigated many water damage claims where for the lack of a little extra pipe, a lot of damage could have been prevented. This is a could place to use up some of your PEX scrap pieces, just don't reduce the size of the vent.0 -
Correct me if I'm wrong
but would the check part of the Watts 9D still work if the vent is plugged ?
We stopped using the 9D years ago due to this same nuisance problem . We use the Wilkins double check , ventless backflow preventer . On small residential jobs with a PRV on the feed line , it's the way to go .0 -
check installation
Make sure that the backflow preventer is installed upstream of the PRV. The 9D requires a 12 - 14 psi differential accross it to work correctly (not drip)0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements