When using a LLH do I need a Spirovent or Wye strainer?
binskibok
Member Posts: 19
in Gas Heating
Currently installing a Vitodens 200 in a Cape with 3 zones (copper to runtal, black pipe to convectors) using Grunfoss alpha with zone valves. Should a spirovent and wye strainer be a required part of the system layout or is it a duplication of function since Viessmann requires the use of a Low Loss Header which seems to have similar functionality? I'm looking for the best possible system layout without redundancy or added costs.
0
Comments
-
Not Necessarily
Check out the attached LLH's. They do have a sensor port in the them and I like them better than the Viessmann LLH.There was an error rendering this rich post.
0 -
TRVs
Instead of the 3 zone valves why not use the Vitodens the way its meant to operate, with continuous circulationand TRVs. Especially with the Alpha and the Runtals
The LLH has a manual air vent and by design, trap the dirt and debris at the bottom of the LLH and can be removed with the drain.
JeffreyJeffrey Campbell0 -
Will constant circ work with 1950 type convectors ?
Your mention of constant circ is definately the way to go but I'm limited to 1950 type convectors on the first floor. Until I convert those to newer radient panels with TRVs I fugured the zone valves were the way to go. Being the homeowner I found that this boiler upgrade project has been quite the learning process for me . I will talk to the installers for more feedback. I'm trying to be both green and energy efficient. It seems that I made the right decision by going with Viessmann. Thanks again for your comments and suggestions.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements