How do I clean a mud leg?
arches
Member Posts: 52
The mud leg drain port on our boiler (Smith 28A) has a ball valve. When I open it with the boiler off or (carefully) with the boiler on, I get nothing more than a teaspoon of water. I saw reference to blowing down the mud leg by building boiler pressure with a king valve, but unfortunately this boiler setup lacks one.
Is it asking for trouble to try to manually clear the mud leg with a stout wire or metal rod? Backflush with a garden hose (after the boiler has cooled)? The boiler water is quite dirty, and seems to be getting worse.
There's a drain cock at a low point in the wet return, but I wouldn't be able to drain the boiler below the height of the hoffman loop nipple.
Is it asking for trouble to try to manually clear the mud leg with a stout wire or metal rod? Backflush with a garden hose (after the boiler has cooled)? The boiler water is quite dirty, and seems to be getting worse.
There's a drain cock at a low point in the wet return, but I wouldn't be able to drain the boiler below the height of the hoffman loop nipple.
0
Comments
-
nudge
since i have no experience, i'd probably think it's ok to back flush it with a garden hose .. but i'd probably be wrong .. i hope someone has better answer.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
dislodging sediment from boiler
if it were mine i would get a big pan holding several gallons, and place it under the valve outlet. then i would get a long enough piece of stout wire, and try to push it in; being mindful of the width of the sections. i would keep my hands as far away from any rush of hot water as i could; and be ready to pull the wire out quickly, and shut the valve. once the flow was started. once the water is out then you can take off the valve and look inside, to judge how best to rake out the sediment. there may be a temptation to use a high pressure washer, but maybe not with rubber gaskets, only with nipples between the sections.
just be gentle with any probing on any rubber gaskets there may be between the sections. this might be a situation where some boiler cleaner [approved by the mfg.] could be used to boil out/loosen the sludge.
regular "blowing down" of the boiler drain should keep this under control for the future [not to be confused with the LWCO blow down].
don't forget to heat any new water up to the boil, to minimise oxygen infestation!--nbc0 -
Thanks for the advice.
I'll give that a try. It probably doesn't help that this is just a 1/2" valve (reduced down from a 4" fitting). Ideally the clog will just be in the valve body...but things are rarely so easy! More frequent boiler blowdowns will definitely be in order once I get the valve flowing again.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements