Piping Issues-- LWCO
HawkeyeSteamer
Member Posts: 2
I am currently replacing a Weil McLain EGH-85 steam boiler to replace exactly the same 10 year old unit that was dry fired and cracked 4 sections due to previous piping issues.
I have a fair amount of knowledge in steam systems and refer to "Lost Art" like it was my bible. However I have a curious question regarding the following.
This is a two pipe system that has a Hoffman WCS-8 simplex condensate pump. The old system merely had a MM 101 Feeder and a probe type LWCO. The condensate unit was using the internal float to refill the boiler and the LWCO was wired into the water feeder.
On the new system I would like to use a Hoffman #47-2 float type LWCO with feeder and although the boiler piping recommendations and diagrams in "Lost Art" dictate that it should probably be a 247-2 unit I am restricted by clearances to pipe it in on the right hand side of the boiler as WM would like.
Will I get into trouble pipine the 47-2 into the left side gauge glass tappings as is normal with that unit. I am still going to pipe the condensate pump to the return side of the equalizer and am installing the probe type LWCO in the lower tapping as a secondary safety device.
One question, do I take a chance flooding my boiler if this is piped this way ?
I'm looking for some help... Thanks
I have a fair amount of knowledge in steam systems and refer to "Lost Art" like it was my bible. However I have a curious question regarding the following.
This is a two pipe system that has a Hoffman WCS-8 simplex condensate pump. The old system merely had a MM 101 Feeder and a probe type LWCO. The condensate unit was using the internal float to refill the boiler and the LWCO was wired into the water feeder.
On the new system I would like to use a Hoffman #47-2 float type LWCO with feeder and although the boiler piping recommendations and diagrams in "Lost Art" dictate that it should probably be a 247-2 unit I am restricted by clearances to pipe it in on the right hand side of the boiler as WM would like.
Will I get into trouble pipine the 47-2 into the left side gauge glass tappings as is normal with that unit. I am still going to pipe the condensate pump to the return side of the equalizer and am installing the probe type LWCO in the lower tapping as a secondary safety device.
One question, do I take a chance flooding my boiler if this is piped this way ?
I'm looking for some help... Thanks
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements