1st mod/con. circulators/ zone valves?

I am installing my first mod-con boiler on Monday.  Installing TT prestige solo 175 with

Smart 50 indirect tank, two zones of baseboard and two future zones. Piping primary/secondary.  Trying to decide to zone with circulators or zone valves?

Any thoughts on piping/ zoning?

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 3,019
    Depends

    What type and size zones ?

    There was an error rendering this rich post.

  • plumber11248
    plumber11248 Member Posts: 4
    baseboard.

    existing zones are baseboard, aprrox 85' each. two furure zones are unknown and are only going to be tappings with isolation valves for now.
  • Big Ed_4
    Big Ed_4 Member Posts: 3,019
    edited January 2010
    Loops

    Large Loops and your extra large loops, I would use circulators ...

    There was an error rendering this rich post.

  • CMadatMe
    CMadatMe Member Posts: 3,086
    edited January 2010
    Why Such a Big Boiler?

    Zone with zone valves and use a Grundfos Alpha as your system side pump. The question I have is why such a big boiler? 85 feet of residential baseboard per zone even at a 4GPM flow rate is only 102,000 max output at 180 degree water. I also wouldn't primary/secondary.  I would use a hydro seperator/low loss header. While primary/secondary will work, keep in mind it was primarly developed to protect cast iron boilers from being shocked. A mod con prefers to have the coldest water possible returning from the system to get it's best efficiency.  One of the beefs I have with most mod/con installation manuals is that they don't even offer it in their piping arrangements which is a shame. It isloates the boiler from the system side , collects any debris plus helps in promoting condensing.

    There was an error rendering this rich post.

  • plumber11248
    plumber11248 Member Posts: 4
    LARGE BOILER

    Chris to your question why so big.  Customer is expecting to add an two floor addition of unknown size and has asked that i provide some capasity for the future. I figured with the turndown abilitys of this boiler this would be a safe bet.  The hydro seperator/low loss header sounds great, don't know how expensive they are, but dont have it factored in to my cost, things i will have to think about for the next one.  Any control of choice for the zone circulators?
  • EricAune
    EricAune Member Posts: 432
    Circ relay

    Simple, Taco makes a great line of relays for circulators.  SR503, 4, 5, 6 depending on how many zones you will end up with.  Each will have a priority zone designation if you have DHW.  These relays will keep it as simple as it gets.  

    There was an error rendering this rich post.

  • CMadatMe
    CMadatMe Member Posts: 3,086
    Zone Control

    I had to edit my original post meant to write zone with zone valves but after reading your follow up post I would zone circs knowing that a possible 2 floor addition is being used.  With the possible addition I can understand the increase in boiler size.

    There was an error rendering this rich post.

  • bob eck
    bob eck Member Posts: 930
    circulators

    check out using grungfos ups1558fc three speed circulators with built in check valves for secondary pumps check with triangle tube for what circulator to use going through the boiler heat exchanger also use a grundfos circulator for the indirect water heater.
  • plumber11248
    plumber11248 Member Posts: 4
    MY ORIGINAL TOUGHS

    My local tt rep. is specing taco 0010's for primary and dhw and two 007 for seconadary basboard loops.

    Was just looking at the grunfos alpha, looks like a great pump for the primary and dhw. almost same cost.

    Was originally thinking zoning with zone valves, and just installing a r832a circulator control for single taco 007 secondary pump. Dhw priority would be controled by boiler control, shutting down the primary circulator when there was a call for hot water.

    Was thinking this would be the simplest solutions, and would eliminate , 1 circulator, and four flow controls on the two secondary loops.

    Still needing flow controls on primary and dhw loop.

    Does this seem sound?



     