oil line sizing

fwb1375
fwb1375 Member Posts: 7
I have two oil burners in a basement. The oil line is teed off before the units (3/8)

into two differnt oil ffilters, and then into units. The feed is off of the bottom of the tank,and then runs along the floor about 30 feet away. The units work fine until both run at the same time. I put a pressure guage on one of the two units. When just the one unit runs, i am at 100psi. With that unit running and the other kicking on at the same time, the pressure drops until it snuffs the flame out. My thinking is that if i run new oil lines into the top of tank, and increase to 1/2" and bring to both units that i will eliminate the problem. I am thinking that i may have alot of sludge in bottom of the tank. I was planning to run one 1/2" OD copper line into the top of the tank,and overhead which is 7 feet high with a developed length of 43 feet and then tie in before tee to both units. Doe anyone think this would be a problem?      Any input would be great.

Comments

  • Charlie from wmass
    Charlie from wmass Member Posts: 4,373
    not such a good idea

    You could use a duplex fitting and convert on unit to two pipe or connect both and use a tiger loop. Are you a home owner or a technician? To make sure you meet local fire codes you may want to have a professional do it if you are not one.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • Alan R. Mercurio_3
    Alan R. Mercurio_3 Member Posts: 1,624
    Re: oil line sizing

    You could also have a priority relay installed. Just a thought. :)

    There was an error rendering this rich post.

  • Steamhead
    Steamhead Member Posts: 17,387
    edited December 2009
    Is there

    any vacuum in the line when both burners run?



    Is the shutoff valve at the tank all the way open?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Is this a two on one line system?

    Are both of the appliances operating with a one line system?

    If so, what are the firing rates of the respective appliances?

    Ed Carey