Pressuretrol to Vaporstat

Jfonto
Member Posts: 43
I have a 1980's Weil mclain residential steam boiler; is there any reason not to switch to a vaporstat control.
0
Comments
-
Before we answer that
do you have a one-pipe or a Vapor system? What model W-M is it?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
vaporstat?
It's a one pipe system and I'd have to dig out the literature but part of the model # was 66. I'll get the whole thing if that's not enough0 -
A Vaporstat is more critical
on a Vapor system, but there's no problem using it on yours. But if the boiler is oversized, a Vaporstat can make it short-cycle as pressure starts to build. If that happens, it may be possible to down-fire the burner slightly- when you look at the boiler model, also tell us what make and model burner is on it- for example, Beckett AFG. Take a picture if you're not sure and post it here.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements