Straight pipe either side of pump
Tim Potter
Member Posts: 273
How much does the length of straight pipe on either side of the circulator matter?
Specifically coming out of the boiler buddy and into the brass distribution manifold
1-1/2 copper in & out of a 007 pump.
Thank You
Tim
Specifically coming out of the boiler buddy and into the brass distribution manifold
1-1/2 copper in & out of a 007 pump.
Thank You
Tim
Winter Park, CO & Arvada, CO
0
Comments
-
straight pipe
One book I've read by a well known heating guru in the industry suggests 12 pipe diameters of straight pipe upstream of a pump, and 4 pipe diamters downstream, but I think most in the industry practice about 4-6 pipe diameters upstream and "who cares" downstream, or so it seems.There was an error rendering this rich post.