heating problem

mike09
Member Posts: 8
I have a Coleman Evcon Model #BGU10016A which will light burner and blower starts upon call for heat, however, after 30 seconds burner will go out, and the igniter will start again to light burner which will light and go out after 30 seconds, and after three tries ( i think) the green light blinks in small window, and i guess process stops. Does anyone have suggestions to trouble shoot problem?
Michael in New Jersey
Michael in New Jersey
0
Comments
-
Clean
flame sensor first. If you are not knowledgeable in the field, do yourself a favor and call a pro and have it cleaned / serviced / repaired. It may take $$ off your gas bill...
TimJust a guy running some pipes.0