Closely spaced tees
J_W_P
Member Posts: 4
Quick question on using closely spaced tees. Does it matter which ways the tees face each other? Can you have the water enter the run and out the branch in the first tee and the enter the branch and out the run of the second tee? In most of the diagrams I see, the water flows through the runs of both tees and the branches pick up the secondary circuit
Thanks
Jim
Thanks
Jim
0
Comments
-
YUP IT MATTERS
A hydraulic separator does it better . closely spaced tees also need straight pipe in and out something like ten times the pipe diameter. Gerry Alder0