hammer help
keith123
Member Posts: 103
we just had some work done. the radiators were noisy before. now one of the radiators has hammer at the end of the cylce. what should I be looking for ? this is a one pipe system. thank you for any information
0
Comments
-
pitch...
the first thing to check is rad pitch. rads should be slight pitched or tilted toward the inlet pipe .. assuming this is a 1-pipe system .. i would throw a level on the rad and be sure that they are properly pitched slightly toward the pipe end. don't over pitch, that could cause other problems.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
pitched
Thank you for your reply. it is a one pipe system & it's also pitched. what else can cause it ?0 -
the next question...
what kind of "work" was done? and what parts of your system were tinkered with?1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
we
we had a bathroom addition to the house. 2 radiators relocated & one new one installed. the new radiator & one of the moved radiators don't make a peep. The other one that was moved is the one with the hammer @ the end of the cycle.0 -
pitch again ..
the next place i would consider looking is in the pitch of piping leading to the rad. is there a horizontal pipe from the vertical riser to the radiator that could be improperly pitched and allowing water (condensate) to pool?
let's also make sure that we define what water hammer is .. as I understand it, it is the pickup of water by steam and slamming it against the next solid place in it's path...so it possible that the water in a horizontal is being picked up and thrown into the radiator.
please don't confuse normal expansion/contraction of radiators with the pickup and slamming of water by steam.1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
water-hammer website!!
[url=http://www.kirsner.org/pages/WaterhammerVideo.html]http://www.kirsner.org/pages/WaterhammerVideo.html
this site will open your eyes [and ears] to this phenomenon, and show how destructive it can be.--nbc0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements