SUPER Steam Pros
The Boiler Dr.
Member Posts: 163
Gentlemen
Anyone out there familiar with a Unilux - bent water tube boiler?
I have an existing customer with a brand new 12 million Btuh boiler (installed by others) he is unable to operate because he cannot keep water in it if it modulates above 15%.
The boiler has been boiled out twice in accordance with instructions. The water tests and looks clean. Start up has been tried using both treated and untreated water with the same result. The static water level in the top drum is correct to within 1/2 inch.
The steam outlet is 8" - rising 36" above the flange to a 90 - travels horizontal 6ft then rises another 42 inches using 2-45's and carries on an additional 46 feet where it is connected to an isolation valve mated to an 8" check valve. On the outlet of the check valve the line increases in size to 12" and then dumps into a 14 inch "drop header".
Here is my thought: I am convinced the velocity out of the boiler is too great using only 8" piping. I think the riser off the boiler should have been increased to line size (12") as close to the boiler as possible. Alternatively a drop header should have been used at the boiler.
I am interested in your thoughts and suggestions
Anyone out there familiar with a Unilux - bent water tube boiler?
I have an existing customer with a brand new 12 million Btuh boiler (installed by others) he is unable to operate because he cannot keep water in it if it modulates above 15%.
The boiler has been boiled out twice in accordance with instructions. The water tests and looks clean. Start up has been tried using both treated and untreated water with the same result. The static water level in the top drum is correct to within 1/2 inch.
The steam outlet is 8" - rising 36" above the flange to a 90 - travels horizontal 6ft then rises another 42 inches using 2-45's and carries on an additional 46 feet where it is connected to an isolation valve mated to an 8" check valve. On the outlet of the check valve the line increases in size to 12" and then dumps into a 14 inch "drop header".
Here is my thought: I am convinced the velocity out of the boiler is too great using only 8" piping. I think the riser off the boiler should have been increased to line size (12") as close to the boiler as possible. Alternatively a drop header should have been used at the boiler.
I am interested in your thoughts and suggestions
0
Comments
-
unilux
12,000,000 btu seems a lot to squeeze through an 8" main, without "terminal velocity".
they must have a tech support department-as they have a very cool website.--nbc
[url=http://www.uniluxam.com/videos/impactvideo.html]http://www.uniluxam.com/videos/impactvideo.html
[url=http://www.uniluxboilers.com/]http://www.uniluxboilers.com/0 -
That's what I thought
I could not access their site from Google but thanks to you I was able to get there. I agree it is a very cool site and now I have contact information. Thanks again0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements