Proportional venting for radiators
EricP
Member Posts: 3
If I have this figured out correctly - when using Hoffman 1A vents on every radiator in the building, they should be set according to the SIZE of the radiator and not the locations relative to the boiler? Since a new boiler was installed a few years back, the 'engineer' had us set these things up according to geography! Most of the radiators are the same size through out the building and are not terribly huge so I'm guessing adjusting them to 3 on the 1A will work, and adjust the few smaller 2 rung radiators even slower. Probably could have saved a lot of money just using the Hoffman 40's on all the same size radiators and just installed the 1A'son the radiators that needed manual adjusting. If anyone has any other ideas, I would love to read, thanks much and great web site! :)
Eric in Portland, OR
Eric in Portland, OR
0
Comments
-
venting-radiator location or radiator size?
even more important than the radiator vents, are the main vents on the dry returns. those vents should be capacious enough to let the air out of the boiler steam chest + the main lines themselves as quickly as possible. money spent on "1 extra vent for each main steam line is never wasted" [anon. 1965]
the radiator vents will then be venting the riser+ radiator- a much smaller volume. therefore a third floor radiator could use a bit of extra venting by virtue of the volume of the tall riser.
so the answer to the question posed above is "neither" and "it depends"--nbc0 -
venting worksheet
You may want to have a look at the Excel Worksheet I put together for venting recommendations (both for Gorton and Hoffman 1A's) .. http://www.ypgmedia.com/heatinghelp/ .. if you have any questions about the sheet contact me directly (email is in the sheet). It includes accounting for "runout" lengths such as long risers.
jpf1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
Hi jpf, I can't seem to open the xls sheets. But I have Excel.
Hi jpf, I can't seem to open the xls sheets. But I have Excel.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements